I have a Fluke 187 I think it is, with the data logging. Used it just the other day to measure the inrush on a 1 KVA 480V to 120V control transformer.
When I arrived it had one of the primary fuses blown, a 7A dual element time delay type. Replaced it with the same type, added my current clamp to one of the primary leads and turned it on. Max current it picked up was about 50mA. Blew out both primary leg fuses!
Disconnected primary leads and ohm input terminals to chassis ground. 0.68 ohms on one side and 1.5 ohms to ground. Dead shorted to ground!
Installed new transformer and fuses today, works fine.
Rechecked the old transformer and now it's showing no shorts. Fully potted unit, looks new. I figure it had a hit from an electrical storm that happened the night before. First time I checked it was right after blowing both fuses, the shorted area was probably still hot. Cooled down it looked fine.
I've always heard that a failed electrical component makes a loud thud if tossed into a dumpster. This one went thud loudly.