Broan model 192 in-wall Electric Heater
240-volt
8.33 amps, 2,000 watts, 6,827 BTU/hour (max setting)
50 feet distance from breaker panel to heater
#12-3G AWG conductors
If my calculations are correct, using #12 AWG wire for your expected heater load with the current carrying conductors 50 feet in length is more than adequate. I would use a 10-amp, 240-volt, 2-pole breaker.
[Depending on your electrical panel manufacturer, a 15-amp breaker may be the smallest available.]
Here is a voltage drop formula to determine the Voltage drop (Vⅾ) in both 120 and 240 volt conductors:
- Vⅾ = Calculated voltage drop
- K = Circular mil-ohm per foot (Use 12.9 ohms for copper)
- Q = Skin effect for AC (Use 1.0)
- L = Circuit length in feet (Use one-way distance)
- I = Current load in amps
- CM = circular mils cross-section area of a conductor (Use 6,530 for #12 AWG)
Vⅾ = (2 ∗ K ∗ Q ∗ L ∗I) ÷ CM
The NEC manual that I am referencing allows a maximum safe 3% voltage drop on a 120 volt conductor. You can double the maximum voltage drop to 7.2 volts (as in your case) if the circuit is 240 volts.
3% Vⅾ = 3.6 volts maximum for a 120-volt circuit
3% Vⅾ = 7.2 volts maximum for a 240-volt circuit
Here is my calculation for your particular application:
Vⅾ = (2 ∗ 12.9 ∗ 1.0 ∗ 50 ∗
8.33) ÷ 6,530
Vⅾ = 1.65 volts
This should be well within the safe voltage drop range specified in the NEC manual to carry the expected maximum amperes for 50 feet to your particular wall heater using #12 AWG conductors. Since this is a 240-volt circuit, you would be allowed a maximum 7.2 volts for calculated voltage drop. Remember, you have two current carrying conductors (black and red in your instance) supplying your 240-volt heater.
I say keep the #12-3G AWG romex you have already installed. Just connect the black heater wire to black supply and the red heater wire to red supply, followed by connecting the bare ground supply wire to the heater chassis like the installation instructions dictate.
DO NOT FORGET TO CONNECT THE BARE EQUIPMENT GROUND WIRE!! Wrap the unneeded white wire around the romex poly-vinyl outer sheath on both ends (at the heater and in the breaker panel). I have seen some unneeded wires (like you have) just wire nutted on the ends. I would wrap it back and tape it with electrical tape. What ever you do,
don’t clip off the white wire at either end. You might need it some day if you change out your wall heater to some other 240-volt device that also needs 120-volts for a timer or some such.
Please be careful while prowling around in your circuit breaker panel. If you can, turn off the main breaker first, use a voltage tester, keep one hand in your back pocket at all times, and only use your other free hand when probing in the panel.
If you are unsure about connecting this heater to power, please don't hesitate to call in a professional.
Try the same voltage drop calculations with these other AWG wire sizes:
- #16 - CM = 2,583
- #14 - CM = 4,107
- #12 - CM = 6,530
- #10 - CM = 10,383
- #8 - CM = 16,509
- #6 - CM = 26,251
Click on this online voltage drop calculator web link, scroll to the bottom of the page and enter your amps, wire size, circuit distance and circuit voltage:
http://www.powerstream.com/Wire_Size.htm
Hope this helps.
..
..