Not exactly sure of the connection method you're describing, but it would seem that NEC 210.10 precludes connecting 15A or 20A receptacles to a 30A circuit.
There should be no problem. The breaker protects the wire between the breaker and the outlet, and the outlet type will restrain the current from the device. Having a lesser amperage outlet on a greater service offers no danger, as long as the outlet itself is not overloaded. That is controlled by the outlet type (and hense, its rating).
As an example, if one were to place a 20 amp outlet on a 15 amp circuit, the plugged in device could easily overload the wire ampacity and not trip the breaker. The outlet would not be damaged because it is rated for 20 amps. The wire may melt because it is not. The circuit breaker defends itself. If a 15 amp outlet is put on a 20 amp circuit, and a device that draws 15 amps is plugged in, the outlet is safe, because it is operating within its ampacity, the wire is safe because it too, is operating within its ampacity and the circuit breaker takes care of itself.
The circuit I propose could look something like this:
http://www.audiokarma.org/forums/attachment.php?attachmentid=483321&stc=1&d=1389815960
Wayner