Then the codes have changed from way back when, when I rewired my house and others. I was following national code at the time and it allowed only six receptacles or a total of ten light fixtures per circuit. If what your saying is that it is out of code to put one receptacle on a circuit, I find that puzzling. How do you deal with dedicated circuits for appliances such as air conditioners etc.?
My understanding is that if there is a single receptacle on a 20 Amp circuit then it must be a 20-Amp recept. One duplex receptacle is two receptacles, so the issue is moot in that case.
I have not seen a maximum number of receptacles on general-purpose branch circuits specified in the 2005 NEC (I could have easily missed this, but six seems unduly low). Our local codes (amended from NEC 2002) allow no more than ten
receptacle outlets per branch circuit. The 2005 NEC defines an outlet as "a point on the wiring system where current is taken to supply utilization equipment", receptacle as "... a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke." and receptacle outlet as "an outlet where one
or more receptacles are installed", so the restriction on the actual number of receptacles is essentially unlimited (within the limits of practicality) if I understand correctly.
If you're putting in a dedicated circuit for, say, a laundry in a residence (which is required by NEC in most cases), it
must be a 20-A circuit, per 2005 NEC 210.11(C)(2), and must have no other outlets other than for washing machine(s); according to NEC 210.21(B)(1) "A single receptacle on a branch circuit shall have an ampere rating not less than that of the branch circuit.". Therefore, if you use a singleton on a 20A circuit, it must be rated for 20A. Using a 15A duplex receptacle is apparently OK because a duplex receptacle is two receptacles (even though only one washer - if there's only one - is supposed to be plugged into that circuit).
Just for aggravation, the installation instructions for the new front-loading washing machine we just bought a few days ago says "ELECTRICAL REQUIREMENTS - CIRCUIT - Individual, properly polarized and grounded
15 amp. branch circuit fused with 15 amp. time delay fuse or circuit breaker." Emphasis mine - note the period after "breaker"; not "15 amp. or greater". Would they deny a warranty claim because it's on the 20-A circuit required by NEC? Cute. IMO, NEC trumps Whirlpool; if they are that concerned, they should put a 15-A slo-blo fuse or CB in their appliance.
I'm thinking about pulling a "homeowner's permit" for a fairly involved electric upgrade in my basement, so I've been reading up on this stuff. I did a lot of wiring with my dad on our property (he had been a licensed electrician before getting a PhD and teaching Physics), and working for an electric contractor summers 35 to 40 years ago, which is how I managed to buy a McIntosh stereo while in college. The basics are still the same, but there sure are a lot more details now! Let me tell you, the recent National Electric Code gives the US Tax Code a real challenge for convoluted rules!
Forgive me for getting windy and pedantic. I'm trying to have a good grounding (so to speak) on this stuff before approaching the city for a permit. This is good practice.